go to the Distribution transformers product page Anonymous asked on Sep 13th, 2015 in Distribution transformers

Recommendations required regarding the loading of a transformer.

We have an Oil Type/Medium Distribution 1000kVA Transformer at a site. There is a situation where the predicted / expected load on one transformer will be around 948kVA. As we understand that if the load is known or can be predicted, it is better to choose a transformer that will be loaded to about 75% of its nameplate rating; whereas the NEC maximum allowable continuous load on a transformer is 100% of its rating.

Could you please advise us pertaining to the loading of the transformer as per the below specifications of the transformer. This is important because the manufacturer instructions supersedes as NEC states, that if you do not follow the manufacturer recommendations then you would fall into a code violation of 110.3 (B) for not following manufacturer instruction.

TRANSFORMER SPECIFICATIONS:
Year of Manufacture : 1992
Application : Distribution Transformer
Basic Transformer Concept : oil-immersed, hermetically sealed
Number of Phases : 3-phase
Type : KTMP 18HC 1000
Rated Power : 1000 kVA
Method of Cooling : ONAN
Voltage Ratio - HV/LV : 13800 / 231 V

Tapping Range : +-2x2.5%
Frequency : 60 Hz
Connection : Dyn11
Load Losses (Pk) : 9482 W
No-load Losses (Po) : 1382 W
Standards : IEC 60076
Total Weight : 2930 kg
Weight of Oil : 585 kg

Looking forward for an earliest response, please.

Deia Bayoumi, Global Product Manager

ABB's answer

The transformer is designed for 100% continuous load at specified ambient conditions according to IEC standard. It’s safe to use the transformer at 100% load considering that transformer protective devices are wired and in use and they are not giving any alarm/trip signals.

0 Comments

or
Submit comment cancel

Area expert

  • Deia Bayoumi

    Deia Bayoumi

    Global Product Manager

    Distribution transformers

Contact ABB

If you want to purchase a product, need any pricing information or need help or support from ABB, please contact your local partner.

Haven't found what you've been looking for?

or Ask a question or Contact ABB