go to the Dry-type transformers product page Anonymous asked on Jan 3rd, 2014 in Dry-type transformers

How long can a dry-type transformer be kept energized without load and then connected to a load instantly without interruption?

Joel A. Kern, Global Product Manager

ABB's answer

It is not a problem to keep a dry-type transformer energized for years without load, and then suddenly connect to a high load. Under no-load conditions, only the excitation or magnetization current flows, which is typically about one percent of the rated current. This causes almost no heating in the coils and therefore no thermal aging of the insulation.

Like this answer 1 person liked it already!