Vector group of Generator Step-up Transformer

Why do we take Vector Group of Generator Step UP Transformer as YNd1 or YNd11. Somewhere I have seen YNyn0 also.

Richard Mucha, Global Marketing Manager

ABB's answer

The small letters of the Vector group refer to the lower voltage, in the case of a GSU Transformer, this is the winding connected to the Generator. For a GSU application one would normally expect the Transformer winding that connects to the Generator to be Delta (d) as this would limit phase un-balance and potential fault currents. To have a GSU Transformer with a Star (y) connection on the Transformer LV would be an exception, but could be possible is certain circumstances. The actual requirements / Vector group specification is driven by the EPC / system engineering.

Like this answer 1 person liked it already!

1 Comment

  • Anonymous commented on Jun 8th, 2017

    You forgot the concept of "Step-up" voltage that's why it's customarily used in the delta to wye transformation in GSU X'former.