At what PPM of gas content in oil should the alarm point be set at? At what PPM should we be concerned?

We have ABB GSU Power transformers that have GE M2 Hydran monitoring units on them. We are trying to figure out where to set the proper alarm setting for gas content in the oil.

Andre Steinberg, Marketing and Sales Manager

ABB's answer

Our recommendation would be to take an oil sample from each transformer and make sure that H2 is below 100 ppm and CO below 350 ppm (current levels indicated in the IEEE Guide) - if that is true than set first alarm level to 150-200 ppm and the next to 250-300 ppm. Both would indicate the need for further investigation since Hydran is just a flag like sensor.

If you have any further questions, pls contact directly our Transformer Service center: